Pumps lost communication

Chrisplus4

Active member
Jun 9, 2020
32
College Station, TX
Pool Size
21500
Surface
Plaster
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-40
My pumps lost communication to the intellicenter. When I try to start the pump, I get a click, but pump does not come on. Tried to reset and it was the same. Anyone have any advise on how to establish connection?
 

Attachments

  • IMG_2468.jpeg
    IMG_2468.jpeg
    507.4 KB · Views: 4
  • IMG_2469.jpeg
    IMG_2469.jpeg
    712.6 KB · Views: 4
  • IMG_2467.jpeg
    IMG_2467.jpeg
    514.6 KB · Views: 5
  • IMG_2470.jpeg
    IMG_2470.jpeg
    537.2 KB · Views: 5
  • IMG_2471.jpeg
    IMG_2471.jpeg
    613.3 KB · Views: 4
It was working fine and I had to replace an automated valve, so I flipped the breaker. Added the valve and flipped the breaker back on. I had to reconnect the Wi-Fi and connect to the network. Everything is on line but the pumps are not.
 
Check the pump RS-485 cable connections on the IntelliCenter board. You may have loosened something while working on the PCB.

Show us pictures of the low voltage compartment in the IntelliCenter.
 
What devices are connected to the three RS-485 connectors on the surge card in the back?

1727637339858.png
 
Last edited:
I saw where someone cut all power off and flipped everything but the control panel on after 5 minutes. Then flip the control panel on.

Did that- and it worked! All works great!

Thank you for attempting to help! I appreciate you!