Pump Won’t Power On - No Display
ChadS44
20
Missouri
Chad,
Do you have a salt cell? If so the SWCG transformer is not wired correctly either .. It should be wired through the pump/filter relay, not directly to a circuit breaker..
Just following up. Went ahead and bought a new pump and replaced the existing breaker with a GFCI. Also moved the salt cell wiring to the relay. Does this look correct? I also bought a square D surge protector. I think it connects to its own 240v 20amp breaker. Does this just go in any available space?
ajw22
26,568
Northern NJ
Pentair Intellichlor IC-60
You do not have any power feeding the line side screws 1 & 3 of the relay you have the SWG transformer connected to.
You should not have two wires connected to one terminal on a CB which you did on the pump CB.
You should wire the 20 amp GFCI relay to Line screws 1 & 3 on the first relay.
You can put two wires under one screw on the relay screws. So you connect the pump to the line side screws of the relay.
What is the other wire connected to the 20Amp CB for?
If you need to connect more loads then you create a pig tail wire to pick up the circuit and wirenut together the wires for the devices,
You should place the 20amp CB for the surge suppressor in the position closest to the power feeds into the panel which are at the bottom.
ChadS44
20
Missouri
Hey everyone, someone pointed out that my salt water generator was wired directly to the circuit breaker. I disconnected and moved the wires to the filter/pump relay. Does this look correct? Each wire that Goes to the salt transformer is connected to the load lug on the relay. Do I need something coming from a breaker that goes to the line sides? Thank you.
ChadS44
20
Missouri
On that dual pole GFCI breaker I’ve got the 240v vsf pump (the manual says to wire it directly to the breaker) and I’ve got the primary control transformer on that same breaker.
ajw22
26,568
Northern NJ
You read that too literally. You can wire the VSF pump direct to the breaker through the line side screws of the relay.
That will cause your entire system to go dark if the pump trips the breaker.
You have an unused 120V breaker. What was your intention with that?
You should power the panel from a separate 120V breaker.
Reactions: duckcmmndr
ChadS44
20
Missouri
Ok. Makes sense. So the pump can go to the line side of the relay and then run from the relay to the breaker? There is actually a wire going into the extra breaker. It goes to a GFCI receptacle on my post. So right now, my primary control transformer goes to the 240v breaker. Will I need a separate dual pole breaker for this?
ajw22
26,568
Northern NJ
The panel can run off 120V. The manual describes how to wire it for 120V.
You can then connect it to the line side of the outlet. Or pigtail off the circuit breaker and wire nut together the wires to the outlet and transformer.