In my opinion, the actual amperage will not exceed 14.5 amps.

The Neptune is listed as 13.6 amps, which is probably more realistic than 17.7 amps.
Typically, a motor will pull about 1,000 watts per hp.
At 1.65 HP, the watts will be 1,650 and the amperage at 115 volts will be 1,650/115 = 14.35 amps.
In any case, the minimum ampacity has to be equal to or greater than 17.7 as specified.
Continuous loading of components is usually limited to 80%, so a 15 amp plug should be limited to 12 amps and this only applies up to 86 degrees Fahrenheit.
If the plug is in an ambient temperature higher than 86 degrees, you have to derate the plug accordingly.
At 114 Degrees F, the plug, wires and all components should be derated at 75%.
So, a 15 amp plug at 114 degrees should not be loaded more than 15 X 0.75 X 0.80 = 9.00 amps continuous load.
If a switch or plug is in the sun, it can easily exceed 114 degrees.
In places like AZ, the ambient can exceed 110 degrees and being in the sun can further increase the temperature to over 130 degrees.
In addition to ampacity, you have to limit the voltage drop to 3% on the supply wires.