Pentair Superflo VST Start up Amps?

jake69chevy

Well-known member
May 4, 2017
64
Fresno, CA
Pool Size
25000
Surface
Fiberglass
Chlorine
Liquid Chlorine
I am unable to find the startup amperage of this pump. It claims ‘Max amps 7.1’ on the sticker on the pump? But I am guessing startup is significantly higher?

TIA

It’s a variable speed, wired at 220v on a 30amp circuit breaker. We are trying to determine what circuits are on the subpanel and what the total required amps are to rewire panel.
 

Attachments

  • IMG_0740.png
    IMG_0740.png
    700.4 KB · Views: 1
Use the specified max amps for each device in a load analysis. You do not need to consider transient startup peaks unless specified.

NEC requires all circuits to be loaded to a maximum of 80% of its rated capacity. A 30 amp circuit should have 24 amps maximum specified load.
 