I have researched this topic a bit further since my last post, but have been unable to locate a definitive answer, I have strong doubts that 250.50 (B)-(3) prohibits bonding the pool grid to the system ground, and may only prohibit using the pool's EPG as part of the required system grounding electrodes, but of course, that is not definitive either. It seems the more I read the more confusing this becomes.
250.50 (B) Not Permitted for Use as Grounding Electrodes. The following systems and materials shall not be used as grounding electrodes:
(1) Metal underground gas piping systems
(2) Aluminum
(3) The structures and structural reinforcing steel described in 680.26(B)(1) and (B)(2)
Informational Note: See 250.104(B) for bonding requirements of gas piping.
The informational note attached to 250.50 (B) is of interest, while 250.50 (B) (1) prohibits the use of a metal underground gas pipe as a grounding electrode, 250.104 (B) requires that the metal underground gas pipe be bonded!
250.104 (B) Other Metal Piping. If installed in or attached to a build‐ ing or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to any of the following:
So it would seem 250.50 (B) was not intended to prohibit bonding, it only prohibits the use of those structures and/or components as part of the required system grounding electrodes.
I was surprised by the lack of consensus amongst members of the Mike Holt Code Forum reading this very issue, and some of the individuals posting on those threads are purported to be members of the code making panels that contribute to the NEC, including one engineer that specifically states he is a member of Code Making Panel-5. I don't know if linking to a post on another forum is an acceptable practice, and I don't want to draw the ire of the moderators, but if you are interested that forum has numerous posts dealing with this very question, you will find dissenting opinions on this whole issue. (The forum rules over there do not allow non industry personnel to post, or I would have posted my question there.)
I found one post particularly interesting, the OP talks about a pool installation where the system grounding electrode is within 5 feet of the pool and as such required to be bonded to the EPG as per NEC 680.26 (B) (7), that spurred an interesting discussion.
I would like to clear up a possible misunderstanding about my original question and the intent of bonding the EPG to the system grounding electrode, after which I will refrain from making any additional attempts to clarify this topic as I am not in any way qualified to do so, and I do not frequent the Holliday Inn.
I was only concerned with providing additional equipment protection from voltage surges, while not negatively impacting safety of life. I am not trying to make the pool safer for swimmers, I was only asking if bonding the pool to the grounding electrode system would provide additional protection for the pool equipment in the event of a nearby lightning strike or other event that would energize the pool shell, without diminishing the EPG's ability to perform it's primary function nor introducing a potential risk to swimmers.
It's clear to me that our pool is up to code as it was built, and is safe for swimmers. I am not seeking to make any DIY modifications to my electrical installation, however, I would have hired an electrician to install the bonding jumper, and may still, if I had been able to quantify the benefit, for now there does not seem to be a consensus, and opinions are all over the map. By the way, my electrician is willing to do it, and our AHJ is willing to sign off on the installation, so go figure...
Thank you once again to those of you who replied, while this topic may lie outside of the scope of this forum, there are undoubtably members who are subject matter experts in the NEC and have been involved with every aspect of pool construction and residential electrical installations.