OmniLogic All stop

Never heard of that.

Where did you read about the OmniLogic has the ability to have an emergency stop switch?
 
What do you want to stop and why?

Where do you want the Emergency Stop to be located?
 
I thought i read that the OmniLogic has the ability to have an emergency stop switch. Does anyone know how this is wired?
Thanks.

steve
The OmniLogic has an External Input Interlock contact that can be used to configure software interlocks to shutdown equipment of your choice; maybe this is what you’re referring to? You could certainly use this to implement an emergency stop switch if you wanted to. In my example case, I have a whole-home generator that performs load shedding if the draw gets too high. I have this wired to the external input on the OmniLogic, where I have interlocks configured to shut down the pumps if the load shed triggers.

Here’s an excerpt from the OmniPL manual; it’s the same as the OmniLogic:
 

Attachments

  • IMG_3639.jpeg
    IMG_3639.jpeg
    232 KB · Views: 8
Last edited:
The OmniLogic has an External Input Interlock contact that can be used to configure software interlocks to shutdown equipment of your choice; maybe this is what you’re referring to? You could certainly use this to implement an emergency stop switch if you wanted to. In my example case, I have a whole-home generator that performs load shedding if the draw gets too high. I have this wired to the external input on the OmniLogic, where I have interlocks configured to shut down the pumps if the load shed triggers.

Here’s an excerpt from the OmniPL manual; it’s the same as the OmniLogic:
that is what I am looking for. Thanks.
 
  • Like
Reactions: twillux