New-ish RS6 AUX question

Teddyadams

Member
Mar 8, 2021
8
The Woodlands
Good morning! I have a two year old RS6 & iaqualink. AUX 1 runs my RJ60 SWCG. Yesterday, when the schedule ran to start the RJ60 the relay clicked a few times and then cut off. The relay is not getting constant 24V from the controller, but the AUX light stays on after flashing a few times. (this leads me to believe that it is intentional in the controller, or signaling a failure of some kind)

I suspected it wasn't the relay, but I changed it anyway. - same issue.
I switched the SWCG over to AUX 2 and it works fine and the now waterfall on AUX 1 does not work.
I recently changed the schedule (a week ago), so I thought maybe it was in the scheduling, but it does the same thing in "service mode".
I don't think I changed anything in the settings that adjusts the VSP speed when the SWCG comes on, but I am open to checking again.

Thank you very much for any insight!
 
Make a warranty claim with your builder and Jandy.

There is some problem with the board and the relay driver. The board is not repairable and will need replacement.