We are almost finished with a new pool install. To say the least, things have not gone well, hence the reason I am here. We have a 15K gallon inground pool that has been installed with complete Hayward equipment and the Omni system. The pool is completely installed, and despite a couple issues, it is almost complete. The couple issues have been drug out by the contractor, as well as subs who either don't show up, or don't want to put the time and effort in to troubleshooting the issue. Therefore, I am left at the point that I am trying to resolve these issues myself.
My concern today is the electrical for the pool. I will get into a complete setup in a minute, but in short, the GFCI breaker keeps tripping and will not stay on. The builder installed a 20amp GFCI which started tripping upon startup. To rule out the breaker being the issue, I went and bought a 30amp GFCI and installed, which trips the same as well. If the system is left off for a period of time, it usually takes about 15-20min before the gfci will trip. If you then reset it, it will trip immediately. However, if I place a standard 30amp double pole breaker in, the entire system runs fine, and will run forever without tripping.
I am pretty knowledgeable and handy when it comes to electrical, including knowing loads, limits, wiring capability, etc. I ran, installed, and wired the subpanel for the pool myself, from the main panel on one side of the house, to where the equipment would be located on the other side. I have a 200amp GE main panel with a 60amp breaker allocated for the subpanel, as well as a 125amp GE subpanel (exterior rated). The only items in the subpanel at this time are the breaker for the pool, and a separate stand-alone breaker for an individual exterior outlet. The subpanel came with a ground and neutral bar, both of which are run back to the main panel. The main panel has a grounding rod installed.
I know that the breaker is not tripping due to load, which is obvious. I know that the GFCI is tripping due to neutral/ground issue, but cannot figure out why. I have gone through ALL of the wiring and connections and cannot find any wiring that is loose, improperly installed, shorting out on something, wet, or taking the wrong path. There are also no wires that are left open, or at a "dead end". I have also reviewed all of the wiring recommendations and diagrams for each of the pieces of equipment, and can find no issues. At this point, I am at a loss, and am hoping that some electrical genius can chime in with some advice, or at least something to check out.
My equipment:
- Hayward OmniHub
- Hayward Relay (1)
- 2 Hayward VSP pumps (1 for pool, 1 for waterwall)
- Hayward Chlorinator and cell
- Lights on waterwall and in pool
The wiring is as follows - Main panel to subpanel. Power runs from subpanel 30amp disconnect. Power then runs to a junction box where both pumps, chlorinator, OmniHub, and relay are all pigtailed together, and then power is run out to each device. The relay supplies power to a converter box, which runs power to the lights. Low voltage wires are run from lights, pumps, sensors - and are run to the OmniHub main box to control each device. The control panel/touchscreen is wired in to the OmniHub and powered by same.
My concern today is the electrical for the pool. I will get into a complete setup in a minute, but in short, the GFCI breaker keeps tripping and will not stay on. The builder installed a 20amp GFCI which started tripping upon startup. To rule out the breaker being the issue, I went and bought a 30amp GFCI and installed, which trips the same as well. If the system is left off for a period of time, it usually takes about 15-20min before the gfci will trip. If you then reset it, it will trip immediately. However, if I place a standard 30amp double pole breaker in, the entire system runs fine, and will run forever without tripping.
I am pretty knowledgeable and handy when it comes to electrical, including knowing loads, limits, wiring capability, etc. I ran, installed, and wired the subpanel for the pool myself, from the main panel on one side of the house, to where the equipment would be located on the other side. I have a 200amp GE main panel with a 60amp breaker allocated for the subpanel, as well as a 125amp GE subpanel (exterior rated). The only items in the subpanel at this time are the breaker for the pool, and a separate stand-alone breaker for an individual exterior outlet. The subpanel came with a ground and neutral bar, both of which are run back to the main panel. The main panel has a grounding rod installed.
I know that the breaker is not tripping due to load, which is obvious. I know that the GFCI is tripping due to neutral/ground issue, but cannot figure out why. I have gone through ALL of the wiring and connections and cannot find any wiring that is loose, improperly installed, shorting out on something, wet, or taking the wrong path. There are also no wires that are left open, or at a "dead end". I have also reviewed all of the wiring recommendations and diagrams for each of the pieces of equipment, and can find no issues. At this point, I am at a loss, and am hoping that some electrical genius can chime in with some advice, or at least something to check out.
My equipment:
- Hayward OmniHub
- Hayward Relay (1)
- 2 Hayward VSP pumps (1 for pool, 1 for waterwall)
- Hayward Chlorinator and cell
- Lights on waterwall and in pool
The wiring is as follows - Main panel to subpanel. Power runs from subpanel 30amp disconnect. Power then runs to a junction box where both pumps, chlorinator, OmniHub, and relay are all pigtailed together, and then power is run out to each device. The relay supplies power to a converter box, which runs power to the lights. Low voltage wires are run from lights, pumps, sensors - and are run to the OmniHub main box to control each device. The control panel/touchscreen is wired in to the OmniHub and powered by same.