Hello everyone. I am new to TFP, and also a new home owner that purchased a home with a pool. I am looking for some help.
Forgive me if this is long winded, but I want to make sure I let you know the details, as well as what troubleshooting has been done, and all of the things I noticed in case they are all connected or I have more than one issue.
Pool Details:
I have a 15,000 gallon pool with a raised spa with a spillway from the spa to the pool. The pool is pebble tech, with an in floor cleaning system. The pool pump was replaced in November 2019 with a Pentair 3.0HP intelliflow VSP. The pool is controlled by an Aqualink RS8 controller installed in the kitchen. The pool has a heater, and there is also a separate pump the runs a large waterfall. The pool was built in 2004. (I attached photos of plumbing).
I purchased the home in December 2020. I have done very little in the way of maintenance. I replaced the autofill float after it kept getting stuck, cleaned cartridges in the spring and fall and adjust chemicals as needed. Other than a neighbor lighting illegal fireworks on 4th of July and the debris blowing in my pool causing algae for a week or two, it is pretty self sustaining and easy to take care of. As I live in a very windy, dusty area, after trial and error, I have three different schedules running on the pump. (12A-4AM 1000 RPM @ 8 PSI, 7 AM-1 PM 2550 RPM @ 14 PSI, and 1 PM - 5 PM 2250 RPM @ 12 PSI) I also run these schedules as a flock of doves are constantly trying to live in my spillway, the constant movement of the spillway scares them enough they stopped coming back to my yard.
In October 2020 I stopped the afternoon schedule and lowered the morning schedule down to 1500 RPM. I noticed that the spa was draining into the pool overnight. I also noticed that previously when I wanted to clean the pump basket that when I popped the top off the pump after pressure releasing, that the water would flow from the skimmer line towards the cartridge housing. I found this convenient to get the extra debris in the basket before I closed everything up. Now that the spa was going "backwards" I noticed that the flow is now going from the cartridge housing towards the skimmer. Essentially blowing the debris out the basket into the lines. Once closing the pump lid and turning it all back on, the same debris blew right back into the basket. As I still had a home warranty I called them; a pool company came a couple weeks later; was told that it was the spa check valve. He also noticed the check valve near the Caretaker 5, and mentioned that if spa was bad that other would be too. We went ahead and replaced them. I cleaned the pump basket after he left, and it seemed to halt the flow out the pump basket when the lid was opened, but the pool took a little longer to prime, but assumed that was due to the lower RPM the schedule was set to, and him opening valves up. However, everything was functioning as normal (pressure, RPMS, flow, popups, GPM, etc) so I let it go.
About a week later, huge wind storm, next day I was out there brushing and heard air in the caretaker pipes, and noticed that when I cleaned the pump basket again a little longer to prime, yet everything was normal.
Two weeks later, another dust storm with a lot of debris. I work 12 hour days so its dark before and after work so I didn't check it for a couple days. Come out, debris in pool, and skimmer is filled to the top, and just a small amount in the pump basket. Cleaned everything out, brushed the pool and cleaned out pump basket, this time priming took forever. It just didn't seem to want to fill at all. I stopped the pump, let it hang out and tried again, when that didn't work I upped the RPMS to 2800 and it worked. There was a lot of air blowing out the returns/popups, and I noticed that the check valve near the Caretaker was half filled with air (attached photo). I switched Aqualink to spa mode everything worked 100% fine let it clean for 30 mins, switched it back to pool mode and everything "fixed" itself, however, I noticed that the GPM was less than normal (65GPM, to 40GPM @ 1500 RPM @ 10 PSI). Went to the skimmer, checked, flow looked normal, weir moving, cartridge housing pressure was normal, everything looked normal.
Googled this, quite a few things come up, however in Spa mode everything is 100% fine so I ruled out the cartridges and seemed to come up that I have a clog in the line or the impeller was clogged. Go outside, turn everything off, pull out skimmer look for clog in skimmer hole (none), take out pump basket and cleaned a golf ball amount of stringy grass debris off impeller. Put it all back together, turned it all back on and now things are much worse. Even less flow out of skimmer, took even longer to prime. It took to almost 3450 RPM to get the water to flow correctly to prime, this time I noticed that the pool pressure is about 10-12 PSI higher than normal, going way over its normal 20 PSI at that RPM, the caretaker valve was showing high as well, and a tiny amount of water leaking out the Caretaker union, and GPM is much lower than normal. Once it primed I immediately returned it back to 1500 RPM and normal pressure. I walked around, low skimmer flow, half air in check valve, but everything was functioning. Lowered it to 1000 RPM, check valve filled as normal. As its been getting down to 20 degrees at night, I made a schedule for 12 AM - 7 AM at 1000 RPM and left it alone.
This past weekend, I decide to try to clear the "blockage". I closed the skimmer and checked the main drain to see what was going on; no improvement on the flow. Closed MD, opened skimmer, no improvement. I left MD opened a little and cycled skimmer on and off for about 20 mins, with no change to flow or addition of debris in the pump basket, besides two small leaves in there. Closed the skimmer and MD and return valve (don't normally do this), released pressure and tried to get pump basket off. The system would not let air out, after fighting with the lid, eventually I opened all valves, pressure released and as usual all the debris rushed into skimmer line, so it was useless. Put it all back together, turned it all back on and now things are much worse. Even less flow out of skimmer, took even longer to prime, the pressure skyrocketed to 38 PSI @ 3450 RPM, I turned it off. I switched it to spa mode turned it on at 1500 RPM @ 10 PSI and it primed at 65 GPM and blew out tons of air out the returns in the spa, let it run until no bubbles. Stopped and tried in pool mode, and it was just blowing air through the popups with only 12 GPM now. The check valve was mostly air, but normal pressure at caretaker and pressure release. I stopped it, waited to see if the check valve would fill, nothing. Started it again at 1000 RPM, with 7 GPM, the check valve filled and everything was functioning in a limited low flow capacity (popups working, but barely). I have tried a few times since then in Spa mode and it functions 100% normal as it should. I switch back to pool mode and it goes right back to this new state of barely limping.
There are no visible leaks, I use pool lube on the o ring of the cartridge housing as well as the pump basket. Visually everything looks fine, except the no flow and how dirty my pool is becoming.
With all of that said, Is there some error on the part of the tech replacing the check valves or is this a blockage I can't clear or something else like air leak? I feel like I am running out of things to troubleshoot, and I make it worse when I open the pump basket.
Thanks
Forgive me if this is long winded, but I want to make sure I let you know the details, as well as what troubleshooting has been done, and all of the things I noticed in case they are all connected or I have more than one issue.
Pool Details:
I have a 15,000 gallon pool with a raised spa with a spillway from the spa to the pool. The pool is pebble tech, with an in floor cleaning system. The pool pump was replaced in November 2019 with a Pentair 3.0HP intelliflow VSP. The pool is controlled by an Aqualink RS8 controller installed in the kitchen. The pool has a heater, and there is also a separate pump the runs a large waterfall. The pool was built in 2004. (I attached photos of plumbing).
I purchased the home in December 2020. I have done very little in the way of maintenance. I replaced the autofill float after it kept getting stuck, cleaned cartridges in the spring and fall and adjust chemicals as needed. Other than a neighbor lighting illegal fireworks on 4th of July and the debris blowing in my pool causing algae for a week or two, it is pretty self sustaining and easy to take care of. As I live in a very windy, dusty area, after trial and error, I have three different schedules running on the pump. (12A-4AM 1000 RPM @ 8 PSI, 7 AM-1 PM 2550 RPM @ 14 PSI, and 1 PM - 5 PM 2250 RPM @ 12 PSI) I also run these schedules as a flock of doves are constantly trying to live in my spillway, the constant movement of the spillway scares them enough they stopped coming back to my yard.
In October 2020 I stopped the afternoon schedule and lowered the morning schedule down to 1500 RPM. I noticed that the spa was draining into the pool overnight. I also noticed that previously when I wanted to clean the pump basket that when I popped the top off the pump after pressure releasing, that the water would flow from the skimmer line towards the cartridge housing. I found this convenient to get the extra debris in the basket before I closed everything up. Now that the spa was going "backwards" I noticed that the flow is now going from the cartridge housing towards the skimmer. Essentially blowing the debris out the basket into the lines. Once closing the pump lid and turning it all back on, the same debris blew right back into the basket. As I still had a home warranty I called them; a pool company came a couple weeks later; was told that it was the spa check valve. He also noticed the check valve near the Caretaker 5, and mentioned that if spa was bad that other would be too. We went ahead and replaced them. I cleaned the pump basket after he left, and it seemed to halt the flow out the pump basket when the lid was opened, but the pool took a little longer to prime, but assumed that was due to the lower RPM the schedule was set to, and him opening valves up. However, everything was functioning as normal (pressure, RPMS, flow, popups, GPM, etc) so I let it go.
About a week later, huge wind storm, next day I was out there brushing and heard air in the caretaker pipes, and noticed that when I cleaned the pump basket again a little longer to prime, yet everything was normal.
Two weeks later, another dust storm with a lot of debris. I work 12 hour days so its dark before and after work so I didn't check it for a couple days. Come out, debris in pool, and skimmer is filled to the top, and just a small amount in the pump basket. Cleaned everything out, brushed the pool and cleaned out pump basket, this time priming took forever. It just didn't seem to want to fill at all. I stopped the pump, let it hang out and tried again, when that didn't work I upped the RPMS to 2800 and it worked. There was a lot of air blowing out the returns/popups, and I noticed that the check valve near the Caretaker was half filled with air (attached photo). I switched Aqualink to spa mode everything worked 100% fine let it clean for 30 mins, switched it back to pool mode and everything "fixed" itself, however, I noticed that the GPM was less than normal (65GPM, to 40GPM @ 1500 RPM @ 10 PSI). Went to the skimmer, checked, flow looked normal, weir moving, cartridge housing pressure was normal, everything looked normal.
Googled this, quite a few things come up, however in Spa mode everything is 100% fine so I ruled out the cartridges and seemed to come up that I have a clog in the line or the impeller was clogged. Go outside, turn everything off, pull out skimmer look for clog in skimmer hole (none), take out pump basket and cleaned a golf ball amount of stringy grass debris off impeller. Put it all back together, turned it all back on and now things are much worse. Even less flow out of skimmer, took even longer to prime. It took to almost 3450 RPM to get the water to flow correctly to prime, this time I noticed that the pool pressure is about 10-12 PSI higher than normal, going way over its normal 20 PSI at that RPM, the caretaker valve was showing high as well, and a tiny amount of water leaking out the Caretaker union, and GPM is much lower than normal. Once it primed I immediately returned it back to 1500 RPM and normal pressure. I walked around, low skimmer flow, half air in check valve, but everything was functioning. Lowered it to 1000 RPM, check valve filled as normal. As its been getting down to 20 degrees at night, I made a schedule for 12 AM - 7 AM at 1000 RPM and left it alone.
This past weekend, I decide to try to clear the "blockage". I closed the skimmer and checked the main drain to see what was going on; no improvement on the flow. Closed MD, opened skimmer, no improvement. I left MD opened a little and cycled skimmer on and off for about 20 mins, with no change to flow or addition of debris in the pump basket, besides two small leaves in there. Closed the skimmer and MD and return valve (don't normally do this), released pressure and tried to get pump basket off. The system would not let air out, after fighting with the lid, eventually I opened all valves, pressure released and as usual all the debris rushed into skimmer line, so it was useless. Put it all back together, turned it all back on and now things are much worse. Even less flow out of skimmer, took even longer to prime, the pressure skyrocketed to 38 PSI @ 3450 RPM, I turned it off. I switched it to spa mode turned it on at 1500 RPM @ 10 PSI and it primed at 65 GPM and blew out tons of air out the returns in the spa, let it run until no bubbles. Stopped and tried in pool mode, and it was just blowing air through the popups with only 12 GPM now. The check valve was mostly air, but normal pressure at caretaker and pressure release. I stopped it, waited to see if the check valve would fill, nothing. Started it again at 1000 RPM, with 7 GPM, the check valve filled and everything was functioning in a limited low flow capacity (popups working, but barely). I have tried a few times since then in Spa mode and it functions 100% normal as it should. I switch back to pool mode and it goes right back to this new state of barely limping.
There are no visible leaks, I use pool lube on the o ring of the cartridge housing as well as the pump basket. Visually everything looks fine, except the no flow and how dirty my pool is becoming.
With all of that said, Is there some error on the part of the tech replacing the check valves or is this a blockage I can't clear or something else like air leak? I feel like I am running out of things to troubleshoot, and I make it worse when I open the pump basket.
Thanks