Putting the heater on the back burner for now. Will add it eventually whether it be this year or next. Does look like the dig will begin jan 6th. Will post pics. Getting excited and stressed already. Lol.
You might consider at least running the conduit for a dedicated 220V/60A service to the equipment pad on the off chance you go with a heat pump. The trenches are going to be dug anyway and electrical conduit is dirt cheap. You just need the conduit and a nylon pull line. Then all an electrician would have to do is either hang another subpanel on the house or wire into an existing set of breaker slots and pull some wire. No need to dig up the yard a second time. However, if you go gas, then you’ll be trenching the yard again. Gas lines need to be installed and pressure tested while the trench is still open in a lot of jurisdictions and so it’s not something you can cheaply install in the ground if you decide to not use it later. A spare electrical conduit is always useful.