I have an Intermatic 104 timer and recently i noticed that it stay on after it was supposed to shut off the pump. the only thing that would shut it off was when I turned off the breaker.
I bought a new Intermatic 104 switch and the problem was the same. wiring was confirmed correct, so what was the problem?
I have a remote lighting system........turns out it has a bypass that will turn the pump on as well as the lights and it had bypassed the Intermatic timer. When I turned off the breaker to the lights, the switch now works.
Has anyone else had this random issue?