Solar uses a 10k thermistor mounted on the roof and measures the temperature available on the roof.
The solar temperature sensor connects to the solar temperature input terminal in the automation box.
A 10k thermistor changes resistance based on the temperature. See chart.
If the solar temperature is above the water temperature and the water temperature is below the set point, the solar circuit should be activated.
So, you can use a resistor to trick the sensor into reading a specific temperature.
Use the resistors to trigger the temperature by putting the resistors in parallel.
The 15k ohm resistor would always be in the circuit and you would use a single pole single throw relay and add a 7.5k ohm resistor in parallel.
The relay coil will be activated by the external 24 VAC control signal.
A 15k ohm resistor and a 7.5k ohm resistor in parallel will read as 5k ohm.
You would get a relay that's activated by the available 24 volt power signal.
When not powered, the reading is 15k ohms, which corresponds to 60 degrees Fahrenheit.
When 24 volts is applied to the coil of the relay, the relay switches the 7.5k ohm resistor to be in parallel with the 15k ohm resistor, which is read as 5k, which is interpreted as 106 degrees Fahrenheit.
So, you're just using the resistors in place of the temperature sensor.
This activates the solar mode and the pump changes to the speed set for the solar circuit.
You can even use a three way valve and valve actuator to bypass the fph if you want by connecting the valve actuator to the solar valve controller.
When the solar circuit is triggered, the valve opens to send flow to the fph.
The solar temperature sensor connects to the solar temperature input terminal in the automation box.
A 10k thermistor changes resistance based on the temperature. See chart.
If the solar temperature is above the water temperature and the water temperature is below the set point, the solar circuit should be activated.
So, you can use a resistor to trick the sensor into reading a specific temperature.
Use the resistors to trigger the temperature by putting the resistors in parallel.
The 15k ohm resistor would always be in the circuit and you would use a single pole single throw relay and add a 7.5k ohm resistor in parallel.
The relay coil will be activated by the external 24 VAC control signal.
A 15k ohm resistor and a 7.5k ohm resistor in parallel will read as 5k ohm.
You would get a relay that's activated by the available 24 volt power signal.
When not powered, the reading is 15k ohms, which corresponds to 60 degrees Fahrenheit.
When 24 volts is applied to the coil of the relay, the relay switches the 7.5k ohm resistor to be in parallel with the 15k ohm resistor, which is read as 5k, which is interpreted as 106 degrees Fahrenheit.
So, you're just using the resistors in place of the temperature sensor.
This activates the solar mode and the pump changes to the speed set for the solar circuit.
You can even use a three way valve and valve actuator to bypass the fph if you want by connecting the valve actuator to the solar valve controller.
When the solar circuit is triggered, the valve opens to send flow to the fph.