panic_button
Bronze Supporter
- Jun 23, 2019
- 354
- Pool Size
- 21000
- Surface
- Plaster
- Chlorine
- Salt Water Generator
- SWG Type
- Pentair Intellichlor IC-40
Second - if you're within the scheduled hours and the pump should be running but it isn't, then is the time correct on the pump? You'll need to disconnect the comm wire to get control of the pump to set it. I thought it might set automatically from the app - but it doesn't. Time is set correctly, and schedules set on the pump. Pump will run when 485 is NOT connected, app shows pump not attached no green light and IC40 will not run due to not receiving pump signal. Once 485 is attached the pump stops, and in the app the pump has a green dot, and is set to disabled and IC40 shows that pump needs to be running for it to generate.
Finally - water temp of -1F? Do you have an explanation for this or could it indicate a bigger problem either with the IntelliConnect or the app or the comms between the two? I was testing to see what would happen if I added a Water Temp Sensor, I think the -1 is the default if there is not one attached.