Hotspot FPH pool heater install

I have a new theory of what might be going on...

I noticed on my system, that after running in air cooled mode for a while, the line that goes through the NC solenoid and bleeds the normal condenser is frosty, which I wouldn't expect since that solenoid should be closed. And when shutting off the system, I can actually hear and feel refrigerant moving through that line. So I seem to have a bad solenoid valve that's stuck open. I'll have it replaced as soon as I can and see how things do after that.
 
Last edited:
  • Like
Reactions: cmc0619 and riny
It's good you found a potential cause. I just went back and compared your installation photos to mine though and I have a question. What is this connection, marked with the green arrow? I think that's an extra connection that I didn't have, so I'm curious where it goes.

1661798028057.png
 
It's good you found a potential cause. I just went back and compared your installation photos to mine though and I have a question. What is this connection, marked with the green arrow? I think that's an extra connection that I didn't have, so I'm curious where it goes.

View attachment 450086
That's an over or under pressure sensor which was on the AC system when it was new, and wasn't part of the FPH install.
 