Heat pump wiring help

jacobg

Bronze Supporter
Mar 31, 2021
21
Lodi, CA
Pool Size
22000
Chlorine
Salt Water Generator
SWG Type
Pentair Intellichlor IC-40
I think I’m doing this correctly but flipping the breaker causes main panel 200A service disconnect to trip, indicating a short or I’m overloading the panel (I’m not)

I had electricians run 50ft of 6 AWG wire from main panel and they installed a 50A breaker. Heat pump hadn’t arrived yet which is why it’s not wired.

Plumber got the plumbing working but now have to wait a week or two for electricians to come back and wire the heat pump. I thought maybe I could do this myself.

They brought four wires from main panel, two blacks, a white and a green. I installed a 60A non fusible disconnect and connected the two black wires. I connected green to the disconnect ground. I ran a whip from heat pump with 6 AWG red and black to disconnect and 8 AWG green. Connected red and black to HP L1 and L2 and green to ground. Connected other end to service disconnect.
I’m thinking I did all I could and should wait for them to come back, but just wanted to throw this out in case someone spots something easy I can try.

thoughts?
 

Attachments

  • CF11C217-CCA6-4537-AF8F-0DD016BD1FE1.jpeg
    CF11C217-CCA6-4537-AF8F-0DD016BD1FE1.jpeg
    503.3 KB · Views: 27
  • EABFAA9C-48FF-4CC5-BFDF-3E0ADF72597F.jpeg
    EABFAA9C-48FF-4CC5-BFDF-3E0ADF72597F.jpeg
    348.9 KB · Views: 24
  • 61867685-4828-4D4D-B293-31C9755E4D9E.jpeg
    61867685-4828-4D4D-B293-31C9755E4D9E.jpeg
    719.9 KB · Views: 22
  • F432713F-70AC-4C66-A837-16E14974494A.jpeg
    F432713F-70AC-4C66-A837-16E14974494A.jpeg
    158.6 KB · Views: 20
  • 08F6E62B-0E2B-4F09-9109-5DE954E29507.jpeg
    08F6E62B-0E2B-4F09-9109-5DE954E29507.jpeg
    147.7 KB · Views: 21
  • DA1C9156-D469-4F74-8CB5-B9BDA5D74881.jpeg
    DA1C9156-D469-4F74-8CB5-B9BDA5D74881.jpeg
    513.4 KB · Views: 22
  • 8EA6D638-E48A-4E05-9EC4-C18A4498243C.jpeg
    8EA6D638-E48A-4E05-9EC4-C18A4498243C.jpeg
    181.2 KB · Views: 21
  • 786E401A-DD25-4F70-8B38-E8EF874B2290.jpeg
    786E401A-DD25-4F70-8B38-E8EF874B2290.jpeg
    244.2 KB · Views: 24
they installed a 50A breaker
That doesn't look like a new breaker.

If it's tripping right away, it's a short.

Overloads are a thermal trip caused by heat. That takes time.

Short circuit trips are magnetic and happen very fast.

You can check for short circuits, but you have to know exactly what you're doing or it can be very hazardous.
 
It’s tripping immediately. I tested continuity on the two black wires at the service disconnect and no tones with breaker off.

The electricians said they had to drive 40 minutes away to find that breaker but I’m with you, it looks completely old and busted even though they just installed it last week.

Part No is DPX-075

Cant read the X.
 
Is the 50 amp breaker tripping when the 200 amp breaker is tripping?

If not, I would be concerned if it's working correctly.

Maybe it's just a little bit slower than the 200 amp breaker, but with how it looks old, you might want to replace it.

I think that the breaker is the below if the two single breakers are 20 amps each.


The Square D by Schneider Electric Homeline Quad-Pole Tandem Circuit Breaker consists of (2) single-pole, 20 Amp and (1) double-pole, 50 Amp breakers. Requiring only 2 pole spaces, it is used for overload and short-circuit protection of your electrical system.
 

Enjoying this content?

Support TFP with a donation.

Give Support
The 50 was not tripping at the same time as the 200. I found one of these 50/20 at a Home Depot an hour away and bought it for in store pickup. I’ll have the option for a new one tomorrow if wiring correctly doesn’t work.
 
The two singles are 20. It is old and overcrowded but the solar PV company I’m going with said it doesn’t need to be upgraded 🤷‍♂️
 