Hayward pump and automation

Read https://www.totallyhayward.com/tech... Updates for Pool professionals July 2020.pdf

Hayward has seen some instances where the HUA from a Gen 3 VS pump was not visible to the Omni control.

These instances have occurred after:

  • A power brownout
  • The pump was installed with incorrect dipswitch position and the dipswitch was moved while power to the pump was still on.
Once Power was restored, or the pump powered down and back up the HUA would not populate into the control.

Solution that Hayward found is that power needs to be turned off to the pump for a MINIMUM of 5 minutes and as much as 15 minutes to allow the drive to reset. Once power is restored the HUA was visible to the Omni and the pump worked normally.
 