Good afternoon all.
First post. I’m wiring in my easytouch 8 panel. All devices have a dedicated gfci breaker. Main power in panel is a surge suppressor breaker. I’m installing the heater power and fireman’s switch. Can I run both in the same conduit. I know through my own experience, you are not supposed to run low voltage DC and AC together. It’s not a communication wire. Just a on off switch. Only wanted to run one conduit if possible. Just trying to keep things tidy.
 
Welcome to TFP.

Fireman's switch is low voltage - 24V. You should not mix high voltage 120V circuits in the same conduit with low voltage circuits.

So no. Safe trumps tidy.
 
No problem. There’s plenty of room. I had just read something about using shielded 300v rated wire was okay to use. Thank you for the reply.