Note that the ampacity is based on the wire's temperature rating and the ambient temperature that the wire will be exposed to.
The rating is at a temperature of up to 86 degrees Fahrenheit.
For wires that will be exposed to higher temperatures, you have to derate the wire based on the chart.
For example, at a temperature of 96 to 104 degrees, you derate at 88%, which is 50 x 0.88 = 44 amps.
It looks like your wire is rated to 90°C conductor temperature at 20°C ambient.
So, it is rated to 60 amps at up to 86 degrees.
However, it has to be sized at the 75 degree rating, which is 50 amps.
What is the temperature rating of the lugs on circuit breakers?
Are breakers rated for 90C wire?
Product Line and Environment:
All Circuit Breakers
Resolution:
The wire temperature rating allowed for use in circuit breakers lugs is 75°C.
While it is acceptable to use 90°C wire, that 90°C wire must be sized as if it is 75°C wire.
This is according to the UL standard for circuit breakers, which is summarized as follows:
(1) Breakers rated 125 A or less must be marked for use with 60°C, 60/75°C, or 75°C only wire.
(2) For breakers rated more than 125 A, the proper wire temperature rating is 75°C and the marking is optional.
(3) Wire with a higher temperature rating can be used (e.g. 90°C), but the ampacity of the wire must be based on the wire temperature marked on the breaker.
Therefore, as marked on the breaker, the wire must be sized as 75°C wire.
Even when using 90°C wire, the wire must be sized as if it is 75°C wire.
So, your #6 AWG Aluminum wire can be used up to 150 feet at up to 104 degrees Fahrenheit and the maximum breaker is 70 amps assuming a dedicated circuit for an UltraTemp 140 Heat pump.
You need to read the label on your heat pump to see the specified minimum circuit ampacity and the maximum allowable circuit breaker.