Thank you to everyone on this forum, I have learned so much. Most recently I learned the solar company who added solar heat and anew pump failed to bond the equipment. I have what is likely a silly newbie question but I cannot figure it out. My Pentair Solartouch clearly says it needs to be bonded, “
Grounding and Bonding to the SolarTouch® Controller
Connect a ground wire from the primary electrical panel to the SolarTouch Controller
ground bus bar. Also ground each piece of high voltage (120 VAC or 240 VAC) equipment
that is connected to the Controller relays. The SolarTouch controller must also be
connected to the pool bonding system using an 8 AWG (minimum) wire. An earth terminal
for bonding is provided on the grounding bus bar inside the SolarTouch controller.”
However when I look in the box, it looks like the pic on pg 16 here: https://www.pentair.com/content/dam...stem_Installation_and_Users_Guide_English.pdf
I can’t figure out where the bonding wire connects. Is it to the ground screw? If so the 8 AWG is too large to fit. Thanks for the help.
Grounding and Bonding to the SolarTouch® Controller
Connect a ground wire from the primary electrical panel to the SolarTouch Controller
ground bus bar. Also ground each piece of high voltage (120 VAC or 240 VAC) equipment
that is connected to the Controller relays. The SolarTouch controller must also be
connected to the pool bonding system using an 8 AWG (minimum) wire. An earth terminal
for bonding is provided on the grounding bus bar inside the SolarTouch controller.”
However when I look in the box, it looks like the pic on pg 16 here: https://www.pentair.com/content/dam...stem_Installation_and_Users_Guide_English.pdf
I can’t figure out where the bonding wire connects. Is it to the ground screw? If so the 8 AWG is too large to fit. Thanks for the help.