When I select Pool on the Temperature control panel the fan will run. I get no voltage on the ignitor terminal on the ignition module. After about 50 sec. I do get a 26 volt reading at the gas valve but it only lasts for about 5 seconds. I'm assuming this is because I'm not getting any ignition. It appears to go through the cycle several times and eventually shuts down giving an error message of E-04. Indicating a fan problem ...but the fan runs fine.
I have already replaced the temperature control board, which was obviously defective, and I was thinking that the ignition control module may be gone as well because I can't get the 120v reading at the ignitor terminal on the module. What else could cause not getting the required 120v reading at the ignitor terminal on the ignition module.
Thanks in advance for your assistance.
I have already replaced the temperature control board, which was obviously defective, and I was thinking that the ignition control module may be gone as well because I can't get the 120v reading at the ignitor terminal on the module. What else could cause not getting the required 120v reading at the ignitor terminal on the ignition module.
Thanks in advance for your assistance.