Wire for Pool Pump..

RED800

0
Jul 20, 2012
3
Camden, NY
i have romex 12/2 from my panel box, through my house to the inside of my attached garage, from that point can i run the required THWN wire? I am going to put it in conduit 12-18" deep to an outlet that my pump will plug into. i am in upstate NY
 
Anything inside the dwelling can be romex, but inside the conduit will need THHN/THWN. Since this is 12/2, I'm guessing it's a 220V circuit with the two legs and a ground. And, I am also guessing it is protected by a 220V 20A 2P GFCI breaker. If not, you should change out the breaker. 20A is the limit for 12 gauge.
 