Morning.
I'm replacing a handy 400 LXI with a Handy 400 JXI. 10 years old...its run its life.
The guy installing the new heater noted that the 3\4" line that the initial pool installer ran is to small and suggested two options.
1. have gas company install a 2 PSI meter and then drop back tot he required pressure with a regulator at the heater
2. install a new 1.25" line.
Either way i'm going to have to do one of the 2 but looking for opinions.
If i have a new meter installed - im hoping the gas company can drop the pressure back to standard before it enters the house....would hate to have to install regulators at all of the devices in the house
And if i install a new line....it's only a 25 foot run and the meter and heater are on the same outside wall...but unable to bury thew new line and it will have to go on the outside of the brick,...which unfortunately means i have to run the line directly behind the heater ( between the heater and the brick of the house ) and i have no idea if that might violate any code.
I plan on trying to get in touch with some in Houston planning department to ask about code but I've found that they really aren't geared up for answering questions at the Houston city planning dept.
What bothers me most about this is that ive looked up the pipe requirements of the current heater ( lxi 400) and it calls out the 1.25" pipe. i didn't try and cheap out when i built the pool, i didn't even know this was an issue till now ...but seems like my pool builder either didn't know the requirement or tried to save a few bucks.....and really - its 25 feet. why not put in the proper line!
Appreciate any thoughts on the most efficiency way yo get back in my hot tub!
Cheers
Mac
UPDATED
there was actually 1 1\4 all the way from the meter to the riser at the heater. It was choked back the 3\4 at the heater riser...so all good.
Sadly i don know how to close a thread but no further action required.
Appreciate the replies...
I'm replacing a handy 400 LXI with a Handy 400 JXI. 10 years old...its run its life.
The guy installing the new heater noted that the 3\4" line that the initial pool installer ran is to small and suggested two options.
1. have gas company install a 2 PSI meter and then drop back tot he required pressure with a regulator at the heater
2. install a new 1.25" line.
Either way i'm going to have to do one of the 2 but looking for opinions.
If i have a new meter installed - im hoping the gas company can drop the pressure back to standard before it enters the house....would hate to have to install regulators at all of the devices in the house
And if i install a new line....it's only a 25 foot run and the meter and heater are on the same outside wall...but unable to bury thew new line and it will have to go on the outside of the brick,...which unfortunately means i have to run the line directly behind the heater ( between the heater and the brick of the house ) and i have no idea if that might violate any code.
I plan on trying to get in touch with some in Houston planning department to ask about code but I've found that they really aren't geared up for answering questions at the Houston city planning dept.
What bothers me most about this is that ive looked up the pipe requirements of the current heater ( lxi 400) and it calls out the 1.25" pipe. i didn't try and cheap out when i built the pool, i didn't even know this was an issue till now ...but seems like my pool builder either didn't know the requirement or tried to save a few bucks.....and really - its 25 feet. why not put in the proper line!
Appreciate any thoughts on the most efficiency way yo get back in my hot tub!
Cheers
Mac
UPDATED
there was actually 1 1\4 all the way from the meter to the riser at the heater. It was choked back the 3\4 at the heater riser...so all good.
Sadly i don know how to close a thread but no further action required.