You read things wrong... Per the NEC- 2014/2017 versions.
Any pool with greater than or equal to 42 inches of water must be bonded.
Direct burial cable is not acceptable for use around pools. Direct burial cable has an un-insulated ground conductor and code requires that only insulated ground conductors be used.
A wooden deck has nothing to do with bonding at all and does not exempt you from needing bonding.
The electrical grounding system is NEVER directly connected to the bonding system of the pool. In the US current code there are no grounding rods in any part of a bonding system.
A quick break down of AGP bonding goes like this:
Loop of #8 bare copper wire arund the entire pool buried 3-6" down and 18-24" from the wall of the pool
Connect that loop to the wall/frame of the pool in 4 spots spread equally around the pool (in your case just the wall)
Connect your equipment (pump, heater, SWG) to the loop
Connect your water bonding fitting to the loop
Connect any thing metal permanently installed a within 5 feet of the pool to the loop such as ladders, fences, metal conduit,or decorative metal flamingos. Things like patio furniture or tables that you move around don't count.
Everything in the loop is connected with #8 bare copper wire
Split bolt connectors will be used where two pieces of wire come together
Only connect to equipment at the factory installed bonding fitting