Ok, thanks for the update. Hope the fuses fix the problem.
I received the fuses today. I replaced the FC2 blown 1.5A fuse, hooked up the old transformer and got power to the panel (that's the good news).
To test it, I turned on the spa via the Jandy control panel and then manually used the keypad to put it in spa mode. When I did this, I got an error the keypad that said BD. I checked the board and now FC4 was blown (transformer secondary).
Decided to pull out the old transformer and try the new thinking that may help. Replaced the blown FC4 fuse and the same thing happened. So it's not the transformer.
Looking at the manual for BD code, it says if FC4 is open proceed to "open FC4 section"
It then says to check for faulty ignitor and faulty blower wiring. They looked ok.
It then says to check for resistance of the ignitor and the blower. For the blower it gives number ranges and the measured resistance was within the ranges they gave so it looks like the blower is ok. They did not give numbers for the ignitor... it said Measure resistance across ignitor. If shorted, replace ignitor". I measured 17ohms which is within the 10.9-19.7 ohms i found elsewhere on the internet.
The last thing it says is replace control module. I hope this isn't the control board, as it's new!?!
Ed