Will a 61,000 BTU heat pump extend the swim season in Seattle for a 15,000 gallon AGP?

TerranGuy

Active member
Jun 30, 2021
33
Seattle, WA
Pool Size
17000
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
CircuPool RJ-30 Plus
Quick question,

The pool will be a 24' round above ground pool. It's a ThePoolFactory Aurora (all resin). It'll be buried half way down 2'3" and backfilled with soil. I'm also adding wall foam. The pool will also have a solar cover at all times it isn't in use. It gets sun about 95 percent of day. My budget is $2,000-$3,000 for the heat pump, but my real constraint is space. I'm installing the heat pump under a deck, and unfortunately that limits me to a horizontally venting heat pump. I'm very close to buying a Raypak Crosswind 65-I. (Raypak – - Crosswind 30-I, 40-I, 50-I, 65-I)

The Raypak calculator says that with an average water depth of 5' (there will be a 6' maximum deep end) - I should be okay to open pool in April or May, and close in October. But what do you say from experience? I'm hoping to run my pump for only 8-12 hours a day. My equipment is a Circupool SmartFlo Variable Speed Pool Pump, a CircuuPool CJ-2750 Cartridge Filter, and a CircuPool RJ-30 Plus Salt Chlorine Generator.

Also, do I just use a partially open diverter to allow the pump to run at a higher GPM than the heat pump allows for?

Thanks everyone!
 

Attachments

  • PXL_20210705_203946407.jpg
    PXL_20210705_203946407.jpg
    743.7 KB · Views: 15
  • Pool Design-2.jpg
    Pool Design-2.jpg
    55.4 KB · Views: 14
  • Raypak-Calculation.png
    Raypak-Calculation.png
    52.5 KB · Views: 14
  • 204285574_10158142006336188_8499269096471648946_n.jpg
    204285574_10158142006336188_8499269096471648946_n.jpg
    59.2 KB · Views: 14
.I'm installing the heat pump under a deck, and unfortunately that limits me to a horizontally venting heat pump. I'm very close to buying a Raypak Crosswind 65-I. (Raypak – - Crosswind 30-I, 40-I, 50-I, 65-I)

Page 7 of the manual says...

This unit requires a minimum of 12" (305 mm) of clearance from walls, shrubbery, equipment, etc. around the entire perimeter of the heater. This allows for ample air intake. Ample clearance around the air outlet is required to prevent recirculation of air. We recommend not placing the unit underneath eaves, decks, or porches, as this causes recirculation of discharged air, thereby reducing the efficiency of the heater, or even stopping it.

The 61K BTU HP for your 16,000 gallon pool will give you at best 1/2 degree per hour of heat.

I think the HP will be marginal for your pool where you want to place it.
 
Thank you so much for the response! The picture doesn't do a great justice to the size under the deck, but the heat pump will have 2'+ of clearance on all sides/top as well as 11' in the horizontal exhaust discharge direction. What size pump do you think would be best? They have a 2 HP unit.

If I'm planning to keep the pool at temperature for the entire season, should I be worried about the 1/2 degree per hour at best heat rate?
 
Last edited:
Thank you so much for the response! The picture doesn't do a great justice to the size under the deck, but the heat pump will have 2'+ of clearance on all sides/top as well as 11' in the horizontal exhaust discharge direction.

The sentence I highlighted in red is not about clearance it is about airflow around the HP. Being under the deck and boxed in on three sides there is little airflow to prevent the HP from recirculating its discharged air.

It is not an optimum location and will likely effect the efficiency and performance of the HP.

What size pump do you think would be best? They have a 2 HP unit.

If I'm planning to keep the pool at temperature for the entire season, should I be worried about the 1/2 degree per hour at best heat rate?

The more BTU's the better.
 