Hello all, I have a pool with raised spa that share a pump. I purchased a Hayward SP3200VSP last year to run with my ProLogic controller. It has worked great - until I installed the OmniLogic Retro Upgrade kit. When I try to turn on the pool pump with the OmniLogic controller, the relays click and the pump clicks but nothing happens. I was able to discover the pump during the configuration of the OmniLogic controller and it displayed the HUA which I selected for the pump. I have it as a VSP and priming for 2 minutes in the config but it won't run. All other pumps (water feature, cleaner, lights, blower, etc. seem to be working fine). Any help with this would be greatly appreciated.

Chris
 
Welcome to TFP.

Do you have a pump RPM speed set in the pool schedule?
 
Last edited:
Thanks for the reply - I found the issue - my VSP was connected to the ProLogic controller relay but, per Hayward, it should be on it's own circuit breaker and controlled with the Low Voltage Relay onboard. I wired it up this way and it is now working with all speeds.
 