Tingly Light

Apr 29, 2016
93
Houston, TX
Pool Size
17500
Surface
Plaster
Chlorine
Liquid Chlorine
Howdy. The light in my pool (pictured) gives off an uncomfortable electrical sensation when my hand is about 4 inches from the rim of it. I turned off the circuit at the breaker box but the tingle persists. As far as I can tell, the only other thing on the pool light circuit is a GFCI outlet immediately below the light switch (pictured) which never has anything plugged into it - so, only two connections total on the 20A circuit (pictured). Pool light works fine, though I plan on changing the bulb at some point for a wallet-friendly LED. Any troubleshooting tips to help understand and then fix the issue? Thanks.
 

Attachments

  • 20240630_163404_copy_750x1000.jpg
    20240630_163404_copy_750x1000.jpg
    179.3 KB · Views: 7
  • 20240630_163342_copy_750x1000.jpg
    20240630_163342_copy_750x1000.jpg
    207.7 KB · Views: 7
  • 20240630_163130.jpg
    20240630_163130.jpg
    338 KB · Views: 7
You can do either first, but both should be tested.

When you turn off the master breaker, removing power from the house, does it go away? If not, call the power company, there is stray voltage, likely from a transformer nearby.
Second turn off the breaker, is the electrical sensation still exist? You may have circuits sharing a neutral. You could be bleeding through the neutral/ground bar of the main breaker instead of the hot leg.
CFCI may be faulty, easy replacement.
 