Hi,

I had a single speed pump controlled by an Intermatic P1353ME 3-circuit with a fireman's wire to the Raypak. The Intermatic has a timed cooldown function that's (was) reasonably fool proof. How can I do this with a recently upgraded Superflow VS? There's not much documentation out there on this topic. I think I can manually time the Intermatic against the RPM/time programming on the VS but I don't think I should trust that. Can it signal from the COM port on the VS or would reliance on the heaters pressure switch be a decent enough redundancy? Is there a smart or proper way to do this?

Thanks,
Patrick
 
I think I can manually time the Intermatic against the RPM/time programming on the VS but I don't think I should trust that.

That is what most folks do.


Can it signal from the COM port on the VS

No, that will not work.

or would reliance on the heaters pressure switch be a decent enough redundancy?

Not recommended and unsafe.

Is there a smart or proper way to do this?

You might use a current sensing relay....

 