Here is another poorly designed swimming pool. As the title suggests, I wonder what the smallest distance between pump and pool should be.
Background: Our pool equipment is located 5' above the pool surface due to the slope of the lot, visible in the lot survey below. The pool surface is 87' above sea level, you can relate all other elevation marks to this. The 5' negative head has created the following problems:
) suction lines (future return lines) to existing equipment site and keep filer and heater there. The image below shows some proposed locations.

Here is another poorly designed swimming pool. As the title suggests, I wonder what the smallest distance between pump and pool should be.
Background: Our pool equipment is located 5' above the pool surface due to the slope of the lot, visible in the lot survey below. The pool surface is 87' above sea level, you can relate all other elevation marks to this. The 5' negative head has created the following problems:
- Several extra check valves increase power consumption.
- Sensitivity to vacuum leaks. The slightest dirt or tiny pine needle in the the lid o-rings introduce air and massively increases power consumption. I regularly see over 300W @ 25 gpm according to the Pentair Intellifow VSF display. We installed new pumps, no improvement.
- Very hard to prime. We have the pumps running 24/7 for this reason.
- 'A' benefits from existing suction lines already surface at 'A' for check valves, minimum re plumbing would be required. A is only 2' horizontal from the water surface. I have never seen a pump this close to open water and wonder of there is a reason. I read NEC Section 680 and found the following:
- "The maintenance disconnecting means must be readily accessible and located within sight" OK, checks out.
- "at least 5 ft from the permanently installed pool": OK
- "Underground wiring isn’t permitted under permanently installed pools or within 5 ft horizontally from the inside wall of the pool unless necessary to supply the permanently installed pool or storable pool equipment. If space limitations prevent underground wiring from being at least 5 ft away, wiring must be installed in complete raceway systems of rigid metal conduit, intermediate metal conduit, or PVC conduit." OK
- 'B' would be my second choice because relatively modest re-plumbings requires only lawn digging.
- 'C' is 6' below pool surface. Requires removing a deck as well as hand digging under the pool to re route suction lines. My least favorite option for that reason. There is no room to run pipes over due to trough and tall concrete columns.
- Would location A with its proposed shut off be code compliant?
- Do you see any other reasons not to opt for location 'A'?
- What are your opinions on B and C?
- Do you have any other solutions for solving this pump problem?