Want to tackle installing the IntelliCenter myself because quotes to install were outrageous. I know I void the warranty by doing it myself which is why I want to ensure I'm on the right path before embarking. I figure if done right, it will outlast the year warranty.
I read through the manuals of the equipment and the IntelliCenter Quick Reference/Information Guide. With that I did my best to formulate what I think is a sound plan of attack. I was planning to use GFCI breakers on all equipment that touches water. There are no protections in the subpanel. Please let me know your thoughts.
My equipment is as follows:
Powering the IntelliCenter / Pool Lights / GFCI Outlet: I didn't see any notes requiring a GFCI here. Therefore, I was going to grab a Siemens Q2020 to provide 120v from one of the poles. The other pole I was going to connect to the GFCI outside that will be mounted to the case. From the GFCI, run lines to a relay that will control the pool lights. This will provide GFCI protections and how I interpreted the MyAZPools did it. Note: I do have a 4 pole Eaton that I can reuse to save a little bit of money. Let me know if I should reuse that instead.
Filter Pump: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to filter pump to provide constant power. Use a serial cable to connect to the RS-485 from the pump to the Comm Port J4 on the IntelliCenter. I found these on Amazon (Link), that I think will work? Although, they aren't the colors the manual calls for, it shouldn't be an issue as long as they are wired correctly on both ends.
Water Feature: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to connect to relay. Relay to pump
Spa Equipment: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to connect to relay. Connect both Spa Pump and Blower to the same relay???
Heater: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF. However, I cannot find any conclusive notes, but I assume it would be similar to the filter pump where it needs constant power. The manual says to use RS-485 to communicate between the units. However, according to this post, there is only a fireman's switch on the heater which will go to the J2 - Gas Heater terminal on the IntelliCenter???
Actuators: Appears to be self explanatory. Match Return and Intake to Return and Suction sides. I do need an additional for the heater bypass valve. This will go under Valve A
Temps: Air probe stays near the low voltage exit on the IntelliCenter. Water is between filter pump and filter itself.
Edit: TLDR of my setup for future researchers. Disclaimer, I'm no expert
I went with 3 Siemens QF220 GFCI, 2 Siemens Q120, and 1 Siemens QSPD2A065. I attached some photos of my IntelliCenter.
1st QF220 goes to Line side of the Filter Pump relay.
With the Pentair IntelliFlo VSF connected to Line side as well.
Cable from Amazon used to splice RS-485 to J4 on the IntelliCenter.
Jumped the Load side of the Filter Pump relay to the Line side of the 1st relay.
Line side of 1st relay also connects the Pentair Master Temp 400.
Same Amazon cable to connect Fireman's Switch.
2nd QF220 goes to Line side of relay 2.
Spa pump on Load side of relay 2.
3rd QF220 goes to Line side of relay 3.
Spa blower on Load side of relay 3.
Jumped Line side of relay 3 to Line side of relay 4.
Water feature to Load side of relay 4.
1st Q120 powers the IntelliCenter.
2nd Q120 connects to Line side of GFCI receptacle.
Load side of the GFCI to Line side of relay 5.
Load of relay 5 to the pool lights. This provide GFCI protection to the pool lights.
I read through the manuals of the equipment and the IntelliCenter Quick Reference/Information Guide. With that I did my best to formulate what I think is a sound plan of attack. I was planning to use GFCI breakers on all equipment that touches water. There are no protections in the subpanel. Please let me know your thoughts.
My equipment is as follows:
- Pentair IntelliFlo VSR (Filter pump)
- Pentair SuperFlo (Water feature)
- Pentair MasterTemp 400
- Hayward Max-Flo XL (Spa pump)
- Unknown blower - Will likely replace with Air Supply Silencer 1 hp
Powering the IntelliCenter / Pool Lights / GFCI Outlet: I didn't see any notes requiring a GFCI here. Therefore, I was going to grab a Siemens Q2020 to provide 120v from one of the poles. The other pole I was going to connect to the GFCI outside that will be mounted to the case. From the GFCI, run lines to a relay that will control the pool lights. This will provide GFCI protections and how I interpreted the MyAZPools did it. Note: I do have a 4 pole Eaton that I can reuse to save a little bit of money. Let me know if I should reuse that instead.
Filter Pump: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to filter pump to provide constant power. Use a serial cable to connect to the RS-485 from the pump to the Comm Port J4 on the IntelliCenter. I found these on Amazon (Link), that I think will work? Although, they aren't the colors the manual calls for, it shouldn't be an issue as long as they are wired correctly on both ends.
Water Feature: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to connect to relay. Relay to pump
Spa Equipment: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF to connect to relay. Connect both Spa Pump and Blower to the same relay???
Heater: Use Siemens QF220 GFCI breaker or The Pentair PFG PA220GF. However, I cannot find any conclusive notes, but I assume it would be similar to the filter pump where it needs constant power. The manual says to use RS-485 to communicate between the units. However, according to this post, there is only a fireman's switch on the heater which will go to the J2 - Gas Heater terminal on the IntelliCenter???
Actuators: Appears to be self explanatory. Match Return and Intake to Return and Suction sides. I do need an additional for the heater bypass valve. This will go under Valve A
Temps: Air probe stays near the low voltage exit on the IntelliCenter. Water is between filter pump and filter itself.
Edit: TLDR of my setup for future researchers. Disclaimer, I'm no expert
I went with 3 Siemens QF220 GFCI, 2 Siemens Q120, and 1 Siemens QSPD2A065. I attached some photos of my IntelliCenter.
1st QF220 goes to Line side of the Filter Pump relay.
With the Pentair IntelliFlo VSF connected to Line side as well.
Cable from Amazon used to splice RS-485 to J4 on the IntelliCenter.
Jumped the Load side of the Filter Pump relay to the Line side of the 1st relay.
Line side of 1st relay also connects the Pentair Master Temp 400.
Same Amazon cable to connect Fireman's Switch.
2nd QF220 goes to Line side of relay 2.
Spa pump on Load side of relay 2.
3rd QF220 goes to Line side of relay 3.
Spa blower on Load side of relay 3.
Jumped Line side of relay 3 to Line side of relay 4.
Water feature to Load side of relay 4.
1st Q120 powers the IntelliCenter.
2nd Q120 connects to Line side of GFCI receptacle.
Load side of the GFCI to Line side of relay 5.
Load of relay 5 to the pool lights. This provide GFCI protection to the pool lights.