Between the SQD and the intermatic I would go with the SQD one. Easy to install and is indoor/outdoor rated. I may be biased as that is the one I have in my main panel at my house.
The other question would be if it's over kill to have another one on the sub panel for the pool.
The majority of transient events will make their way into your electrical system through your service entrance panel to the house. That should be your highest priority for quality surge protection. Transients can also be generated within your house/pool equipment area so locating a quality surge device there can have benefit.
It is also possible for nearby lighting strikes to a tree, house etc to induce a transient into nearby electrical circuits and damage equipment. If you have a pumping system on the far side of your house electrically distant from your main panel an induced surge could damage all of your equipment because the SPD upstream offers no protection.
On a side note, all of the surge devices you guys have been posting would offer virtually no protection for a direct lighting strike of moderate strength. You would need a SPD of at least 100kA per mode which are not residential class SPDs. I'm not even putting a device that large on my home. I'm more concerned with transients coming in through the utility system.