I have a pentair mastertemp 250 that I have a very in depth issue. it has the new 6 button control pad and corresponding fenwal. At first I was having sporadic err ignition issues. The heater would fire and heat to temp, but then after losing temp and attempting to re-fire it would give me err ign. I could restart, and it would work at first until getting to temp and then would eventually fail again. I also noticed that it was running HOT, not hot enough for it to overheat, but around 350-400. eventually it overheated (scorched some wires that were touching the furnace) and melted the cover on the fenwal box, also burned out the transformer. And now to the current issue, .. .
I have replaced the transformer (it is putting out good voltage)
I have fixed wiring that was scorched and triple checked all other wiring
I have replaced the fenwal (dont know for sure the if last one was dead, but the casing melted enough and there was some scorch on the board that I felt it should be replaced)
I feel the control board is good, but also have a replacement that I can testing with.
Upon startup, i get error AFS. The blower will not come on. I checked values at F1, and F2 and everything seems to be good, but the relay is not closing. If I jump F1/F2 then the blower DOES operate. The control board is getting 120 and 24vac. everything looks good on J7 coming in but i did notice it doesnt appear to have 24 AC going from the control board to fenwal via J1.
Am I correct in assuming that is 24ac from control board TO the fenwal?
If this is the case, then something is causing control board (2 separate ones) from sending that 24AC. we have replaced the ignitor, and SFS, and thermistor. and have bypassed the AGS, pressure switch and hi limit switch.
the airflow switch seems to be working because if I jump f1/f2 for the blower to come in, then I get err IGN and not err AFS.
lastly I have not looked into the gas valve yet.
TLDR summary - replaced fenwal, control board, transformer, and most sensors, and also double checked all wiring and grounds but still get ERR AFS on startup, blower will not turn on.
Can anyone provide any input to point me in the right direction?
Thanks in advance
I have replaced the transformer (it is putting out good voltage)
I have fixed wiring that was scorched and triple checked all other wiring
I have replaced the fenwal (dont know for sure the if last one was dead, but the casing melted enough and there was some scorch on the board that I felt it should be replaced)
I feel the control board is good, but also have a replacement that I can testing with.
Upon startup, i get error AFS. The blower will not come on. I checked values at F1, and F2 and everything seems to be good, but the relay is not closing. If I jump F1/F2 then the blower DOES operate. The control board is getting 120 and 24vac. everything looks good on J7 coming in but i did notice it doesnt appear to have 24 AC going from the control board to fenwal via J1.
Am I correct in assuming that is 24ac from control board TO the fenwal?
If this is the case, then something is causing control board (2 separate ones) from sending that 24AC. we have replaced the ignitor, and SFS, and thermistor. and have bypassed the AGS, pressure switch and hi limit switch.
the airflow switch seems to be working because if I jump f1/f2 for the blower to come in, then I get err IGN and not err AFS.
lastly I have not looked into the gas valve yet.
TLDR summary - replaced fenwal, control board, transformer, and most sensors, and also double checked all wiring and grounds but still get ERR AFS on startup, blower will not turn on.
Can anyone provide any input to point me in the right direction?
Thanks in advance