Panel Wiring

texaggie1994

Member
Apr 22, 2019
10
Porter, TX
Would like to get some opinions about the wiring in my panel, looks like a rat's nest to me.
Particularly would like to know why the jumpers between my cleaner and air blower and the
ones between the spa and pool lights? Are these just line feeds being shared from the same
breaker?
 

Attachments

  • Pool Wiring.jpg
    Pool Wiring.jpg
    559.1 KB · Views: 36
Assuming that you're talking about the wires run between the third relay from the left in the top row and the fourth relay from the left in the top row, it's because they're getting their power from the same break, like you had guessed, but it was wired so you could control them both individually...
 
1994,

To be honest, that is one of the neater EasyTouch panels I have seen on this site... You are not even close to a "rats nest".

Your salt cell transformer is wired correctly, and the pump is getting AC constant power. You have twice as many circuit breakers as most installs, and that is a good thing..

All and all I am impressed with the work. I wish I had of had your electrician when they initially wired my ET... :mrgreen:

Thanks,

Jim R.
 
The wiring could be a little bit neater but that's just a cosmetic issue. maybe a couple zipties wouldn't hurt. Really not worth it though.

The jumpers are normal and perfectly acceptable.

As Jim said I've seen much much worse than that. The panel was installed well and wired correctly.
 