The alternating 40/80 usually means the the circuit board is not getting a good reading from the stack flue temperature sensor.
Check the stack flue temperature sensor with a good ohmmeter while the sensor is cool. It should read 3.8 megaohms.
Check the wires from the circuit board to the sensor to make sure that they are not damaged.
I would replace the sensor if the wires are good.
If it still has problems, replace the circuit board.