Great for wanna be pool builders of all ages. Kit comes complete with undersized SWG, cheap non repairable valves, equipment pad that fits in half of a standard bathroom stall for minimal storage concerns, and black algae within six weeks of opening. Get yours today before supplies run out! Today only for the first 100 callers, get two kits for the price of one!
/Sarcasm off
Long story short….HOA pool is less than a year old. Construction ran months over deadline. I was called in at the end of last season for a consult for black algae six weeks after the pool was opened. Delivered a 16 page owners rep report detailing deficiencies of the actual build to the blueprinted specifications. Ended up adding the account to my portfolio this year….Opened the panel yesterday after discovering the Inteliflo3 was delivering an under volt error. Found the pump pigtailed to two independent single circuit 20 amp breakers (at least one was gfci so it’s safeish
). Only one was labeled main pool pump….SWG was pigtailed into the same mess so was being backfed through one breaker even though its labeled breaker was off. Builder originally wired the Intelliflo 3 for 120v then must have realized the 3HP pump only runs on 240. Supremely frustrated and disappointed that hacks take folks hard earned money and deliver
.
Pictures of the pad for a giggle. It’s trapezoid shaped. For reference left side is 7 ft long, right side is 5ft, width is 5 ft. Who does this and thinks they know what they are doing!

/Sarcasm off
Long story short….HOA pool is less than a year old. Construction ran months over deadline. I was called in at the end of last season for a consult for black algae six weeks after the pool was opened. Delivered a 16 page owners rep report detailing deficiencies of the actual build to the blueprinted specifications. Ended up adding the account to my portfolio this year….Opened the panel yesterday after discovering the Inteliflo3 was delivering an under volt error. Found the pump pigtailed to two independent single circuit 20 amp breakers (at least one was gfci so it’s safeish


Pictures of the pad for a giggle. It’s trapezoid shaped. For reference left side is 7 ft long, right side is 5ft, width is 5 ft. Who does this and thinks they know what they are doing!