For a 20 amp breaker, a continuous load of 20 amps will not trip the breaker. For a 27 amp load, the breaker can take up to 1 hour to trip. For a 40 amp load, the circuit breaker has to trip within 2 minutes.
So, most likely the initial voltage drop was mostly due to high amp loads for short periods of time.