The AC-250 can deliver different flow volume based on the allowable pressure drop.
The meter will deliver 250 CFH at a 0.5" pressure drop.
The meter will deliver 355 CFH at a 1.0" pressure drop.
If you allow for a 1.5" pressure drop, the meter will provide about 460 CFH.
If you allow a 2" pressure drop, the meter will provide 565 CFH.
If you have a main regulator providing 7" w.c before the meter, you will have 6.5" w.c after the meter.
Plumbing is generally designed to have a maximum pressure drop of 0.5" w.c, which puts the heater inlet pressure at 6.0" w.c.
It depends on the heater pressure requirements and you want the inlet pressure to be at least 1" above the minimum for margin.
Most likely a 250 class meter will work for a 250 heater as long
as it is the only appliance operating, but you want to verify the pressure during operation to verify.
Does your home have gas heat, dryers, stoves, water heaters, gas grills etc?
View attachment 621267
Common BTU ratings
Boilers: 100,000 - 200,000 BTUs/hr*
Boilers (High Efficiency): 80,000 - 160,000 BTUs/hr*
Dryer: 22,000 BTUs/hr
Furnace: 100,000 - 150,000 BTUs/hr*
Furnace (High Efficiency): 75,000 - 100,000 BTUs/hr*
Garage Unit Heaters: 30,000 - 100,000 BTUs/hr
Gas Fireplace (standard) 25,000 - 35,000 BTUs/hr
Generator (standby): 200,000 - 300,000 BTUs/hr
Outdoor Grill: 25,000 - 40,000 BTUs/hr
Pool Heater: 199,000 - 400,000 BTUs/hr
Range: 60,000 BTUs/hr
Range (Commercial): 120,000 - 225,000 BTUs/hr
Spa Tub: 100,000 - 200,000 BTUs/hr
Tank Water Heater: 35,000 - 60,000 BTUs/hr*
Tankless Water Heater: 140,000 - 200,000 BTUs/hr*