noob alert.
Picture shows three wires that come from conduit into my timer.
Old pump was 115v and new is 230v. I made a (possibly bad) assumption that the capped wires (#2 and 3) were for a 30amp 240v breaker but.... the power to those wires was shut off with the same 20a 120v breaker that is feeding line #1. Checked with noncontact voltage tester. Shutting off the dual pole breakers did nothing.
Also when checking with multimeter to either #2 or 3 and the neutral on timer, only reads 22 volts...
I have an electrician coming Tuesday who seems doubtful that the same breaker feeds all three wires.
Mainly just throwing out here if anyone has any ideas. I'm wondering if these wires are just disconnected at the panel. edit: Just checked at the panel and it's wired up
Picture shows three wires that come from conduit into my timer.
Old pump was 115v and new is 230v. I made a (possibly bad) assumption that the capped wires (#2 and 3) were for a 30amp 240v breaker but.... the power to those wires was shut off with the same 20a 120v breaker that is feeding line #1. Checked with noncontact voltage tester. Shutting off the dual pole breakers did nothing.
Also when checking with multimeter to either #2 or 3 and the neutral on timer, only reads 22 volts...
I have an electrician coming Tuesday who seems doubtful that the same breaker feeds all three wires.
Mainly just throwing out here if anyone has any ideas. I'm wondering if these wires are just disconnected at the panel. edit: Just checked at the panel and it's wired up