So pool is not closed in winter. Is 25k inground. How low can I let the water temp go before turning on the heater?
The biggest risk is probably the skimmers. Once you see ice start forming on the water surface, you probably want to keep the pump running full time or close the pool.Interesting. Thanks. My pipes and stuff are underground or indoors so I think not a problem. I was more thinking of the water itself in the pool which this evening was 33°.
Interesting. Getting more interesting.
I checked the ComPool manual, says freeze protection starts if air temp hits 35.
So I checked the ComPool Easy Touch. At the moment, ComPool thinks air temp is 56 when outside it is 39. I suppose because the ComPool is inside the mechanical room and would appear the air thermometer is inside the ComPool.
If this is true, ComPool will never detect 35F so ComPool freeze protect will never activate.
Am running the pump 8hrs/ day at present as we have at this point very little tree debris.
Lowest temp setting on the ComPool is 40.
What is wrong with setting Heater to heat to 40? If it is 40, heater does not come on so no $$ wasted. If below 40, heater heats it up a bit.
The air temperature sensor should be outside in open air. I suggest opening the enclosure to get a look at the sensor and the length of its cable. It might have enough coiled cable to relocate the sensor. And if it doesn’t, you can obtain one that has a long enough cable to properly relocate.At the moment, ComPool thinks air temp is 56 when outside it is 39. I suppose because the ComPool is inside the mechanical room and would appear the air thermometer is inside the ComPool.
If this is true, ComPool will never detect 35F so ComPool freeze protect will never activate.
The air temperature sensor should be outside in open air. I suggest opening the enclosure to get a look at the sensor and the length of its cable. It might have enough coiled cable to relocate the sensor. And if it doesn’t, you can obtain one that has a long enough cable to properly relocate.
Now that is another good question. Maybe the best yet.So what is the concern?
Sounds like a good plan!
4 hrs per day well more than you need as long as the chlorinator can keep up.
Yeah, the problem there is that you have a newish 1-speed pump. A variable speed pump runs at very low RPM just to keep the water moving.Is true that relocating the thermometer and running the pump if air temp < 35 would be fair amount of $$.