Hello I have rebuilt pool (5 years ago)down to the gunite. Plumbing and equipment new. it is in ground 18000 gallon pentair equipment. Pentair Mastertemp pool and spa 400 heater. Pentair intelliflo vsf variable speed and Flo pump and a pentair clean and clear plus cartridge filter CCP 420. my problem is it will not fire now.
Turn on the heater on spa temp 100 degrees.
The blower starts and when it calls for ignition I hear the click of the gas regulator.
(I have watched the gas meter to see if it gets gas and it does)
I also smell gas.
It try's 3 times
No fire and the ignition box blinks 3 times no other LEDs come on
except the service heater lite.
I turn the power off and back on and still same thing.
I changed the igniter and ignition box.
Still no fire
The resistance on the igniter is about 23 ohms.
Any info would be very helpful
Thank you