- Jul 23, 2012
- 10
- Pool Size
- 12000
- Surface
- Fiberglass
- Chlorine
- Salt Water Generator
- SWG Type
- Hayward Aqua Rite (T-15)
The Prologic controller and Tristar 2.70 THP VS pump have ceased communicating. I'm trying to figure out if the issue is on the Prologic controller side or the pump side. The pump runs fine when disconnected from the Prologic and being controlled by its own controller. The wire between the two tests fine. I tested the voltage on the terminal block connector in the Prologic, interface cable disconnected. It is a constant 115V on all 4 of the pins (+12V, A, B, Com) in the Prologic whether or not the Spa Filter button is on or off. When I test the pump by itself (disconnected from the Prologic) the pump's own controller is putting out 50v to the A and B connections when on at full speed and 0v when off. From this can I assume the issue is with the Prologic PCB? If so I plan on ordering the OmniPL Retrofit kit to resolve the problem and upgrade the system. I also noticed that the drain wire was not connected between the COM (pump) and terminal 4 (Prologic controller) terminals by the original installer. Should it be? It has been running fine this way for a few years. Thank you!