Tiki,
I am not sure if that is the whole story or not, but I am glad it appears to be working now..
I see several problems related or not..
1. VS pump should get constant AC power.. Your pump appears to be wired to the load side of your pump/filter relay, when it should be wired to the line side of the relay.
2. You have external control wires wired to your Aux 2 and 3 relays, when the pump has a working RS-485 control.. Does not make any sense and maybe why the pump would not shut off.
3. The control cable for the pump is routed wrong.. It appears to be between the metal breaker cover and the EasyTouch frame. You can even see a mark where the cable may have been cut.. This could have shorted some of the wiring..
4. Not sure about this one.. My guess is that you only have one pump speed for "Pool" set up.. Is that all you want or need?
5. The RS-485 wires, going from the pump cable to the Main Circuit card are also routed wrong.. They look to be pinched between the breaker cover and the EasyTouch frame..
Just like you, I am here to learn. So I'd like you to do me a small favor.. With the EasyTouch's display in AUTO, the pump's display should read read "Auto". If that is true, I'd like you to put the system into the Service mode. wait 30 seconds, and then tell me what happens to the pump's display... Then put the system back into Auto..
It has been fun working with you..
Thanks,