Mark, trying to compare our head calcs - is there a big difference between our numbers for pipe length?
View attachment 609504
I didn't see this before but it looks like you are putting the pipes in series and not parallel. As I showed above, it is a different calculation. You can't just add the lengths of each pipe. It is a more complicated calculation:
Equivalent length of parallel pipes = n^2 / (1 / L1^1/2 + 1 / L2^1/2 + 1 / L3^1/2 + ... )^2
The equivalent length of the 3 pipes (30', 40' & 88') are either 3x45' parallel pipes or 1x5'. The all will have approximately the same head loss at the same total flow rate.
I made some modifications to the pad plumbing since that appears to be mostly ridged rather than flex. For flex, I use an ID of 1.5" because it tends to a little smaller than ridged at 1.61".
Here are the individual plumbing curve components that I get using the filter pressure:
3 Suction lines in parallel: 0.00049
Suction pad combine into pump: 0.00055
Return pad between pump and filter: 0.00027
16.5 PSI elevated at 43": 0.00634
Total Suction Side plumbing curve: 0.00104
Total Return Side plumbing curve: 0.00661
Total plumbing curve: 0.00765
Another way to look at this is that we know from the filter pressure, that portion has a head loss of:
16.5 * 3.21 + 43/12 = 41.7'
Plotting an offset plumbing curve over the pump curve:
Plumbing Head (ft) = 41.7' + 0.00131*GPM^2
Which results in an operating point of 81 GPM @ 50' of head.