16 years. With the top vent, the heater let a lot of rainwater in and the last rainstorm finally rusted it out too far to repair.How long did your previous heater last?
16 years. With the top vent, the heater let a lot of rainwater in and the last rainstorm finally rusted it out too far to repair.How long did your previous heater last?
If you look at the daylight pic there is no green or white. I don't know why the flash makes it look that way, there is not much to see. Yes I think I see a little white on the concrete in the back corner, probably from the old heater. There is no algae, just ficus leaves that keep blowing into the area.The white on the ground looks like calcium scale from a leak.
The green looks like algae from the area staying wet all of the time.
Did the old heater leak?
Yes, that's what the installer added. Tee. Nipple. Cap. Check.9.6.8 Sediment Trap. Where a sediment trap is not incorporated as a part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical at the time of appliance installation.
The sediment trap shall be either a tee fitting with a capped nipple in the bottom outlet, as illustrated in Figure 9.6.8, or another device recognized as an effective sediment trap.
Illuminating appliances, gas ranges, clothes dryers, decorative appliances for installation in vented fireplaces, gas fireplaces, and outdoor cooking appliances shall not be required to be so equipped.
View attachment 548590
View attachment 548591
Look at your gas line routing and that of the diagram in post 23 and the previously provided diagrams.Yes, that's what the installer added. Tee. Nipple. Cap. Check.
I didn't see anything in the quoted text or descriptions that says the supply has to come from the top. I don't think that's a reasonable interpretation but I'm certainly no expert.Look at your gas line routing and that of the diagram in post 23 and the previously provided diagrams.
They are vastly different.
In post 23, the gas comes in from the top, the line to the heater goes out to the side and the sediment trap out the bottom.
Your gas line comes in from the side, the line to the heater goes out the top and the sediment trap out the bottom.
Additionally, your gas line that close to the side exhaust is dangerous.
Regardless of the condensation, your gas line isn't correct.
According to this:I didn't see anything in the quoted text or descriptions that says the supply has to come from the top. I don't think that's a reasonable interpretation but I'm certainly no expert.
Yes, it doesn't seem to be working right to have the exhaust that close to the supply line. I do note that it's the manufacturer that put the gas inlet 2.5" from the vent... Perhaps not a very good design.
No, I believed the equipment swap was a minimal emergency changeover. I thought he'd use a flexi-line for the heater actually. I have a whole house tankless heater using one even. Likewise with a whole house gas generatorMost references show the gas supply coming in from the top.
In my opinion, that is the correct way to do it.
Some references only say to provide a change of direction, which your does, so some people might argue that it is acceptable.
Did you get a permit and an inspection for this installation?
View attachment 548596
No, I believed the equipment swap was a minimal emergency changeover. I thought he'd use a flexi-line for the heater actually. I have a whole house tankless heater using one even. Likewise with a whole house gas generator...
I identified the missing sediment trap issue and had him add one for extra credit. None had been put in place before with everything permitted and inspected in the past so that system is not working around here anyways. In any case, that sediment trap article I quoted I think clears up the rabbit hole of the sediment trap and that's not my issue here.
I think that a permit is required.No, I believed the equipment swap was a minimal emergency changeover.
It is really not in front of the vent, it is below the vent.I think your only problem is the gas line passing in front of the exhaust vent.
How is the line wet all the way back to the arrows?
It still seems excessive to me.In various places the manual warns of condensate from the exhaust and that it can drop to the floor.