I had what I thought was going to be a small project this weekend to change out the junction box, GFCI and switch that feeds my pool equipment. It wasn't properly sealed and got water damage (rust). I've done a good amount of electrical work in the past so this seemed like a pretty simple project. Got everything back together and when I went to test, as soon as I flip the switch for the pool equipment, it pops the GFCI.
The controller is a Jandy Aqualink RS. The switch is a double pole for the 220V power that goes to 3 relays (Filter pump, water feature, blower). One leg of this splits off to feed the transformer that powers the controller.
I've narrowed it down to the transformer I think - if I remove the hot connection to the transformer, but leave everything else wired up, it doesn't trip. I've compared the new wiring to pics I took before changing anything and it looks like I have everything connected exactly the same way it was before. I haven't pulled the transformer out to test it yet, but that seems to be the culprit. It seems really odd that the transformer would suddenly go bad when everything was working fine before swapping the GFCI & switch.
Any ideas of anything else I should test or check besides pulling the transformer and testing it? I was thinking I'd pull the transformer, connect a plug to it so I can plug it into a GFCI outlet to see if it pops, and if not, use my tester to see if it's putting out 24V, is that the right way to test it?
If I do need a transformer, it may take a few days to get one, and I really don't want to leave my filter pump off that whole time. Can I wire my pump (Jandy VSPHP270AUT) directly to the switch to control it manually for a few days? Since it's a variable speed pump, how would it know what speed to run at? Or can that pump only be used with the controller?
The controller is a Jandy Aqualink RS. The switch is a double pole for the 220V power that goes to 3 relays (Filter pump, water feature, blower). One leg of this splits off to feed the transformer that powers the controller.
I've narrowed it down to the transformer I think - if I remove the hot connection to the transformer, but leave everything else wired up, it doesn't trip. I've compared the new wiring to pics I took before changing anything and it looks like I have everything connected exactly the same way it was before. I haven't pulled the transformer out to test it yet, but that seems to be the culprit. It seems really odd that the transformer would suddenly go bad when everything was working fine before swapping the GFCI & switch.
Any ideas of anything else I should test or check besides pulling the transformer and testing it? I was thinking I'd pull the transformer, connect a plug to it so I can plug it into a GFCI outlet to see if it pops, and if not, use my tester to see if it's putting out 24V, is that the right way to test it?
If I do need a transformer, it may take a few days to get one, and I really don't want to leave my filter pump off that whole time. Can I wire my pump (Jandy VSPHP270AUT) directly to the switch to control it manually for a few days? Since it's a variable speed pump, how would it know what speed to run at? Or can that pump only be used with the controller?