If a double pole GFI, the kind you install in the main breaker panel, is rated at 30 amps, is that 30 amps for EACH leg or 30 amps total, 15 amps for each leg?
Thanks.
Thanks.
JohnT said:There are normally 2 neutral connections on a 220V GFCI. One is for the GFCI, and the other is out to the load. With a 2 wire load, you just leave the out neutral unconnected and connect the pigtail to the panel neutral.
A 220 GFCI monitors both hots and the neutral looking for a zero sum. If the neutral isn't used, it still looks for a zero sum on the hots.