    Pump gf tripping

    My Haywood VSR Pump is tripping the gf but only intermittently. It's down this a dozen times in the last two months since the pump was replaced.. Haywood said pump should be wired directly to gf and not go through relay. Thoughts?

  2. Back To Top    #2
    Mod Squad Jimrahbe's Avatar
    Join Date
    Jul 2014
    Location
    Bedford, TX
    Posts
    9,265

    Re: Pump gf tripping

    Key,

    Welcome to TFP... A Great resource for all your pool questions..

    What else is being powered by the GFCI circuit breaker other than the pump?

    Should be nothing but the pump itself. If you are using that same CB to power other things, it can cause intermittent trips.

    Hayward is correct, the pump should be hard-wired to 220 VAC, it should not be controlled by a relay.

    Thanks for posting,

    Jim R.
    Finished in 2015 - 17K Gal, IG, 20' x 25' Almost Rectangular Pool, Pebble finish, three rockport water falls. Pentair Equipment: EasyTouch 4, IC40 SWG, 3 HP VS Pump, CCP520 Cartridge Filter.
    TF100 with SpeedStir and SampleSizer, ColorQ Pro 7, Dolphin Premier Robot Cleaner, added Screen Logic 2, added small 3 person Caldera Spa.

  3. Back To Top    #3

    Re: Pump gf tripping

    VS pumps can cause nuisance tripping with some gfci breakers. Pentair has two breakers that are designed to work with VS pumps.