Heater issue?

What should I say to the gas co. tomorrow morning when I call regarding the output of the 425 meter - they told me it puts out 700k btu?
Ask them to explain the discrepancy between the meter label and their claim of 700 CFH.

If they know what they're talking about, then they can tell you exactly where they got that rating.

If they cannot tell you exactly how they got that rating, then you need to tell them to figure it out and get back to you with a real explanation.
 
And what would be my retort if they say something like, the meter will push out 700k btu if we up the pressure. Or some other explanation that tries to justify the 425.
 
And what would be my retort if they say something like, the meter will push out 700k btu if we up the pressure.
This is what I would say:

"Please explain where you are getting these figures".

They have to be getting the information from somewhere.

Either they are just making things up and pulling imaginary data from thin air or they have a reference that tells them what they are saying.

If they have a reference, tell them to give it to you.
 
As it shows in the manufacturer's document, the rating at a 2" w.c pressure differential is 898 SCFH.

This rating might be acceptable if they increase the inlet pressure to the meter.

Typical inlet is 6.92" (0.25 psi) to 7.5" w.c. (0.271 psi) up to 0.5 psi (13.8 in WC).

The heater specifies a maximum pressure of 10.5" w.c, so the pressure should not exceed that.

Maybe if the meter inlet pressure is 9" w.c to 10.5" w.c, the meter will perform properly.

This will allow a 7" w.c to 8.5 dynamic at the output of the meter and about 6" to 7.5" at the inlet to the gas valve (dynamic), which is in spec.

1697996486777-png.536970




1698001895764-png.536983
 
A general questuon:

It looks like the pipe that connects to the heater, the last 2’3’ coming from the 1 1/4”, is smaller, like 1” or maybe even 3/4”?

Is the case with all of the last bit of pipe that connects to heaters, it gets smaller where it connects to the heater, no matter how big it is before that last bit?
 
Just spoke with gas co., their department that handles new gas and additional gas service, the department that I had to apply for to ad service.

The tech said yes that is the correct meter, and it supplies 351-700k btu.

The 425 listed online is the model number. I asked where on People’s Gas website does it say that the meter gives up to 700k. She said it’s the correct meter for what I applied for.

Unless I ores and ask to speak to an actual engineer who approves the applications for more gas, I may not be able to find out.
Seems like the only way I can find out is to run the correct size pipe and see what happens.

As I said, the tech that came to put this new meter on said, at the time, that they’d be able to
“Up the pressure”.
 
  • Like
Reactions: JamesW

Enjoying this content?

Support TFP with a donation.

Give Support
The concern that I have with the idea that the gas supplier can “Increase the Pressure if necessary” is how do you know if it is necessary?

Is someone going to monitor the gas pressure to make sure that it remains good?

Most likely, the pressure will be ok if the pressure is set to about 9” w.c to 10” w.c.

Here are some contacts that should be able to provide some information.

IMAC Systems, Inc.

90 Main Street, PO Box 1605. Tullytown, PA 19007

1-800-955-4GAS

Phone: (215) 946-2200


[email protected]

[email protected]

 
This is what the gas co. said in their approval letter when we initially wanted to add more gas service to accommodate pool heater.

They installed the meter they said they would.

I may have posted this already.
 

Attachments

  • IMG_1513.jpeg
    IMG_1513.jpeg
    238.4 KB · Views: 10
66 + 75 + 400 = 541 cubic feet per hour minimum gas meter size.

If we allow for a 1" w.c pressure differential, the meter is rated for up to 583 CFH.

Most likely, the meter will be fine if the line is sized correctly at 1.5".

If the pressure is 7" and we allow for a 1" drop through the meter and a 1" drop through the gas line, then the dynamic gas pressure at the heater gas valve inlet should be at least 5" w.c.

In my opinion, that is a little bit low, but it is still within the manufacturer's specifications.

In any case, I would verify the gas pressure under full load to make sure that it is correct from time of install.

I would want and expect the installer to do a full and proper commissioning of the heater as it is placed into service.

1698078683760.png

1698078822230.png

 

Attachments

  • gas_metering.pdf
    1.6 MB · Views: 0
I still want to know what their proof is that it will deliver up to 700k btu.

i called again, I think I talked to the same person 🙄, and she said they supplied the gas meter that would carry the load that I put on the application.

Which is is 400, 66, and 75 k btu.

It’s like they have some secret way to up the pressure or delivery and they won’t divulge it.
 
You increase the pressure at the regulator (Red Arrow).

The meter will deliver 583 CFH at a 1" pressure drop.

If you allow for a 1.5" pressure drop, the meter will provide about 740 CFH.

If you allow a 2" pressure drop, the meter will provide 898 CFH.

If they increase the pressure before the meter to 8" w.c to 9" w.c, I think that it will be fine.

In any case verify the pressure at the heater inlet during operation.

1698104179522.png

1698078683760-png.537130
 
This is what an engineer at Peoples gas replied as per my question about the btu capability of the 425 model gas meter.
My question is first.
His reply is second.
 

Attachments

  • IMG_1519.png
    IMG_1519.png
    116.2 KB · Views: 7
  • IMG_1520.png
    IMG_1520.png
    129.5 KB · Views: 7
  • Like
Reactions: JamesW
So based on what he’s saying in his answer, once we get the 1 1/2” dedicated pipe in, does any tweaking need to be done by gas co. to meter or delivery pressure?
 
If the pressure starts at 7”, then the pressure at the heater will probably be about 5” w.c to 5.5” w.c.

As long as the pressure to the heater during operation is at least 1” w.c over the minimum, it should be fine.

You can increase the pressure to 8” w.c or 9” w.c to be safe.

I would probably want the initial pressure to be set to about 8.5” w.c.

Verify the pressure under load static and dynamic.

The dynamic should not be more than 1” w.c lower that the static.
 