Ok, this is frustrating. I’m installing an Intex 16x32x52” Ultra Frame pool. It has a vinyl liner, metal braces to hold the thing up, and round metal “pipes” inside the top edge sleeve. NEC 680 is as dry as toast, so for an amateur, I can’t make heads or tails of it. So...
First, it looks like I can run romex inside PVC under the pool so long as it’s 12” deep (table 300.5, column 4 row 1). The electrician said it needs to be 18” deep. Who’s right?
Second, my city inspector is requiring a bonding loop. What the heck am I supposed to connect it to? Where the braces insert into the top edge pipes, the tips of the braces are encased in plastic, A, and B, Intex says nothing about it being bonded, and C, there’s no place on the braces to attach a wire. Arrgghhh.
Third, what is water bonding all about. Do I need to do it, and if so, how do you do it?
Fourth, NEC says the cord for the pump can’t be longer than 3’? Why’d Intex send me one that’s 10’ long?
Fifth, the pump exterior is completely plastic, no idea if it’s “double-insulated” (is it likely that it is?), and I see no bonding attachment, so how the blazes do I bond it?
Sixth, assuming I do need to run this goofy bonding cable around the pool, I’ve seen that it needs to be 4” deep or 6” deep. Which?
Seventh, we had a new 20amp breaker installed at the breaker panel specifically for the pool. Is the pool pump the only thing allowed on that circuit (which has a GFCI outlet on it immediately downstream from the cb and from which all the romex for the pool will be run).
Eighth, what else, in plain English, do I need to know?
First, it looks like I can run romex inside PVC under the pool so long as it’s 12” deep (table 300.5, column 4 row 1). The electrician said it needs to be 18” deep. Who’s right?
Second, my city inspector is requiring a bonding loop. What the heck am I supposed to connect it to? Where the braces insert into the top edge pipes, the tips of the braces are encased in plastic, A, and B, Intex says nothing about it being bonded, and C, there’s no place on the braces to attach a wire. Arrgghhh.
Third, what is water bonding all about. Do I need to do it, and if so, how do you do it?
Fourth, NEC says the cord for the pump can’t be longer than 3’? Why’d Intex send me one that’s 10’ long?
Fifth, the pump exterior is completely plastic, no idea if it’s “double-insulated” (is it likely that it is?), and I see no bonding attachment, so how the blazes do I bond it?
Sixth, assuming I do need to run this goofy bonding cable around the pool, I’ve seen that it needs to be 4” deep or 6” deep. Which?
Seventh, we had a new 20amp breaker installed at the breaker panel specifically for the pool. Is the pool pump the only thing allowed on that circuit (which has a GFCI outlet on it immediately downstream from the cb and from which all the romex for the pool will be run).
Eighth, what else, in plain English, do I need to know?