Hayward powerflo matrix pump breaks circuit popping sound

dilsmith3

Member
Jun 15, 2024
20
athens, al
Pool Size
10000
Surface
Vinyl
Chlorine
Salt Water Generator
SWG Type
Hayward Turbo Cell (T-CELL-5)
So new pool and pump. Hayward powerflo matrix 2 speed pump. All new power and circuits/GFCI. Pump and all equipment grounded. Pool been up and running for month. Really no issues. Been dry and no rain though. Last night first real rain. This am pump not on as usual. So gfci is off. Reset at main panel and at gfci. Once plug pump back in receptacle and power on it makes a popping sound at pump and trips circuit. Done this several times. Not sure if the rain is the issue. Or if the pump motor just decided to die. It’s brand new. Any ideas?
 

Attachments

  • IMG_7338.jpeg
    IMG_7338.jpeg
    683 KB · Views: 4
  • IMG_7339.jpeg
    IMG_7339.jpeg
    726.3 KB · Views: 3
  • IMG_7340.jpeg
    IMG_7340.jpeg
    822.6 KB · Views: 4
  • IMG_7331.jpeg
    IMG_7331.jpeg
    595.5 KB · Views: 4
Here was the issue. Opened up back and
Found black wire had been rubbed to copper by zip tie when put together at factory. Manuf error. Got a ticket into Hayward on the pump. Will send them a pic. Maybe a new pump motor as this one sounds rough now. See pic
 